Default How to calculate generator size watt capacity



Advertise Here

Is there an alternate way to calculate the watt - size capacity needed for a generator besides reading the label on the device/equipment? Are the labels exactly accurate for the start up draw?

I suppose for devices with an electrical plug I could use a Kill A Watt meter.

But I need to know the start up amperage draw for my well pump at my BOL and the start up amperage draw for my circulating pumps for my hot water zones for my gas furnace at my year round home. These are hard wired into the house electrical circuits.

Is there a type of VOM the leads to which I could place around the wiring to read how much amperage they draw?
Old 06-21-2011, 12:51 PM
ConservaBill ConservaBill is offline
Prepared
 
Join Date: Jan 2010
Posts: 273
Thanks: 8
Thanked 212 Times in 112 Posts
Default

You should not need to calculate for starting current. Just add up your loads in Kw add 20% and that will be good enough for your use...+ 50% is of course better..

Bigger is better unless you're talking diesel.. then it is not to your advantage to greatly oversize.
The Following User Says Thank You to ConservaBill For This Useful Post:
Old 06-21-2011, 01:15 PM
Robot's Avatar
Robot Robot is offline
Survivor
 
Join Date: Feb 2009
Location: Twilight Zone
Posts: 7,574
Thanks: 20,562
Thanked 10,714 Times in 4,159 Posts
Default

The company I work for manufactures automation and industrial robotics. I need to check but I think fuses and overloads for AC Motors are rated at 250%. There is a brief momentary inrush current on startup.

Look at the motor nameplate then multiply by 2.5 for this momentary draw.


I have a 5KW Generator, I think it has 6KW Momentary Surge capability.

There are AC amp clamps for monitoring draw. Also simply look at at what amperage your breaker panel has for that given device, it should have been rated appropriately.
The Following User Says Thank You to Robot For This Useful Post:
Old 06-21-2011, 01:50 PM
BlackhawkFan's Avatar
BlackhawkFan BlackhawkFan is offline
Prepared
 
Join Date: Jan 2010
Location: Tucson
Posts: 346
Thanks: 437
Thanked 323 Times in 143 Posts
Default

If you want to measure inrush, get yourself a clamp on ammeter. Make sure it's analog (D'Arsenval movement) since the sample rate of a digital can be misleading for your application, and clamp around one and only one conductor at a time.

Here's one from Granger.
http://www.grainger.com/Grainger/EXT...4&ci_sku=1YPF4

Since you're looking for a spike, start your pump/heater up a bunch of times and take the average. Add 10% for margin/error and you're numbers should be okay.

Understand that the spike can be tall/large/big, but what matters here is the width of the spike. How long the current spike exists is how long the generator over-exerts itself to supply the current your inductive device demands.

-----

How I'd choose a generator:

House max power + Pump&Heater Peak (ie, startup) < 90% of generator peak output

AND

House max power + Pump&Heater sustained < 90% of generator sustained output

Satisfy both of the above relationships for a minimum of 10% margin and you should be okay.

-----

Hope this answers your question.
The Following 2 Users Say Thank You to BlackhawkFan For This Useful Post:
Old 06-21-2011, 01:56 PM
TANSTAF1's Avatar
TANSTAF1 TANSTAF1 is offline
Survivor
 
Join Date: Aug 2009
Location: Born in ME,in exile in MA
Posts: 2,748
Thanks: 922
Thanked 1,855 Times in 1,004 Posts
Default

I could just get a 10,000 watt generator and be done with it.

The problem is the more wattage, the more expensive the generator is. Also, they use more fuel.

I have lived at my home for 25 years and have never needed a generator. If i did, I could probably go to a relatively nearby relatives or friends.

My BOL has been there for 110 years and granted it has only had electricity for half of that time, but it too has never needed a generator. I have a hand dug well that I could use for water but plumbed water would be better.

My area just has blizzards or hurricanes so my typical SHTF is relatively short and for a TEOWAWKI, I don't plan to store that much gas - I'll make other arrangement if and when..

I was/am very tempted with the current 3500 watt Champion generator deal for $211 with free shipping, but don't know whether it is big enough. I would prefer a multi-fuel one but for 200 bucks I might go for something rather than the best or nothing. but not if it is not big enough to power my well pump or my hot water circulators.
Old 06-21-2011, 02:01 PM
TANSTAF1's Avatar
TANSTAF1 TANSTAF1 is offline
Survivor
 
Join Date: Aug 2009
Location: Born in ME,in exile in MA
Posts: 2,748
Thanks: 922
Thanked 1,855 Times in 1,004 Posts
Default

BlackHawkFan,

Thanks. The clamp on ammeter is exactly what I was needing.
Old 06-21-2011, 02:26 PM
Freeholder Freeholder is offline
Target Shooter
 
Join Date: Mar 2010
Location: New Hampshire
Posts: 403
Thanks: 249
Thanked 439 Times in 208 Posts
Default

Well pump in rush current can be up to 3 times normal running current. You would need a peak reading ammeter to measure it as it is very short in duration. A hard motor start can be rough on the pump motor and generator. On my set up I removed the dinky little pressure tank and replaced it with a 60 gallon tank. If I need more water I and can always turn off other accessories if I have to. The big power users are microwave ovens, toasters,coffee makers,blow dryers and the like. I replaced all my old style light bulbs with CFL's. Not crazy about them but they do reduce my electric power requirements. I would not go overboard on a big watt generator they use significantly more fuel than a smaller unit. A 5KW generator is more than enough for most houses if you use wise power management.
The Following User Says Thank You to Freeholder For This Useful Post:
Old 06-21-2011, 02:39 PM
TANSTAF1's Avatar
TANSTAF1 TANSTAF1 is offline
Survivor
 
Join Date: Aug 2009
Location: Born in ME,in exile in MA
Posts: 2,748
Thanks: 922
Thanked 1,855 Times in 1,004 Posts
Default

So, let's say I get a peak reading ammeter and it records that my well pump does briefly peak at 3 times the constant use amperage.

What happens - to either the pump or the generator (if its peak power is not rated at 3 times its constant use rating)?

Does (just) a circuit breaker trip? Does the pump just not start? Does it damage the pump or the generator? How is it hard on the pump motor and generator? Do the coils melt?
Old 06-21-2011, 02:44 PM
BlackhawkFan's Avatar
BlackhawkFan BlackhawkFan is offline
Prepared
 
Join Date: Jan 2010
Location: Tucson
Posts: 346
Thanks: 437
Thanked 323 Times in 143 Posts
Default

While Freeholder is correct about the inrush spike, I wouldn't pay the price of a peak ammeter BECAUSE it's of such short duration.

$$$ vs accuracy...where to draw the line....

Freholder makes a valid observation concerning restricting which appliances/circuits you should consider not using while on generator power.
The Following User Says Thank You to BlackhawkFan For This Useful Post:
Old 06-21-2011, 02:50 PM
BlackhawkFan's Avatar
BlackhawkFan BlackhawkFan is offline
Prepared
 
Join Date: Jan 2010
Location: Tucson
Posts: 346
Thanks: 437
Thanked 323 Times in 143 Posts
Default

Quote:
Originally Posted by TANSTAF1 View Post
So, let's say I get a peak reading ammeter and it records that my well pump does briefly peak at 3 times the constant use amperage.

What happens - to either the pump or the generator (if its peak power is not rated at 3 times its constant use rating)?

Does (just) a circuit breaker trip? Does the pump just not start? Does it damage the pump or the generator? How is it hard on the pump motor and generator? Do the coils melt?
Peak vs constant load is a tradeoff.

The prime mover (gasoline engine) must have the power to turn the generator for peak load.

The generator's windings and insulation must be able to sustain the additional heat and current draw.

Worst case scenario is the prime mover will stop or the generator will overheat, breaking down the insulation, shorting windings.

Don't overthink this one. Use the generator a few times to get used to it. Plan which loads you'll use in an emergency. Listen to the generator. You'll learn to hear when it's loading too much.

Go have a beer. :-)
The Following User Says Thank You to BlackhawkFan For This Useful Post:
Old 06-21-2011, 02:55 PM
BlackhawkFan's Avatar
BlackhawkFan BlackhawkFan is offline
Prepared
 
Join Date: Jan 2010
Location: Tucson
Posts: 346
Thanks: 437
Thanked 323 Times in 143 Posts
Default

Doublepost.
Old 06-21-2011, 03:06 PM
TANSTAF1's Avatar
TANSTAF1 TANSTAF1 is offline
Survivor
 
Join Date: Aug 2009
Location: Born in ME,in exile in MA
Posts: 2,748
Thanks: 922
Thanked 1,855 Times in 1,004 Posts
Default

I am only wanting to run the two items I mentioned. These do not need to run constantly. When they are not, I would power my refrigerator which also does not need to run constantly.

At my BOL I do not even have AC and rarely need it at my house.

If the pumps just peak briefly for a short time and then settle down to a constant (but lower) draw, how would they (have time to) overheat?

As for the price of a peak clamp on ammeter, here's a refurb one for $60. Granted it's digital but it has some method of recording peak or "in rush" current. I do see others at $500.

http://www.icraveit.com/cgi-bin/cate...em=10016964-22
Old 06-21-2011, 03:33 PM
WSierra's Avatar
WSierra WSierra is offline
RESET CONGRESS!!
 
Join Date: Dec 2008
Location: Midwest
Posts: 9,465
Thanks: 13,489
Thanked 12,411 Times in 4,748 Posts
Default

Before retiring, I had access to 'scopes and amprobes etc'. I used those and compared it to readings I took using digital and analog meters. The surge current was not much of an issue... lasted maybe 3-5 cycles typically. It was acceptable, and predictable using the current ratings on the appliances and motors I planned on powering with the smallest practical generators. Refrigeration, minimal lighting, radio/tv, internet... I decided to buy two smaller generators instead of one large one.. saves fuel. Oh, and some lo-o-ong heavy power cords. Works for us. I do not plan on running the AC, 220 appliances, etc. Minimal power usage.
The Following 2 Users Say Thank You to WSierra For This Useful Post:
Old 06-21-2011, 03:38 PM
BlackhawkFan's Avatar
BlackhawkFan BlackhawkFan is offline
Prepared
 
Join Date: Jan 2010
Location: Tucson
Posts: 346
Thanks: 437
Thanked 323 Times in 143 Posts
Default

Quote:
Originally Posted by TANSTAF1 View Post
I am only wanting to run the two items I mentioned. These do not need to run constantly. When they are not, I would power my refrigerator which also does not need to run constantly.

At my BOL I do not even have AC and rarely need it at my house.

If the pumps just peak briefly for a short time and then settle down to a constant (but lower) draw, how would they (have time to) overheat?

As for the price of a peak clamp on ammeter, here's a refurb one for $60. Granted it's digital but it has some method of recording peak or "in rush" current. I do see others at $500.

http://www.icraveit.com/cgi-bin/cate...em=10016964-22
This is precisely the point.

Do as I suggested for your calculations and you'll save yourself some money, have a nifty meter, and have plenty of margin with your power set up.
The Following User Says Thank You to BlackhawkFan For This Useful Post:
Old 06-21-2011, 05:50 PM
Nimmer Nimmer is offline
Set Free
 
Join Date: Dec 2009
Location: Wisconsin
Posts: 1,349
Thanks: 3,111
Thanked 869 Times in 481 Posts
Default

In cold weather states it makes sense to have an LP capable generator because LP is a reasonable price and it stores safely/does not go bad.

I have had a gas generator for decades and at 5,000 watts it will run the
220v well pump no problem. I am looking at having a 110v backup well pump and purchasing either a multi fuel or LP generator soon to have a backup well pump and generator.

After years of thought I am of the same mind of WSierra that smaller is better with backups. When the rubber meets the road using the least amount of fuel to do what is needed is best. Hell even now using less fuel is better.
I am seriously looking to add a second 1000 gal LP tank ASAP just for backup and generator use before the price goes up any higher as it would be an investment that will pay off no matter what.
The Following User Says Thank You to Nimmer For This Useful Post:
Reply

Bookmarks



Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
800 watt portable gas generator VS 45 watt solar panel kit cpellegra Disaster Preparedness General Discussion 21 03-05-2011 07:08 PM
How do I calculate how much water I need? Purdy Bear Wilderness Survival, Hiking and Camping Forum 20 06-10-2009 01:34 AM
Now watt thoughtgirl General Discussion 3 01-07-2009 11:34 AM
E100 generator? (100% ethanol generator) Exists? nattylite General Discussion 3 12-07-2008 04:34 PM
How to size a generator? caduckgunner Disaster Preparedness General Discussion 7 09-18-2008 11:49 PM